T3-BB x Weintek HMI - Issue after updating

T3-BB Firmware updated to Rev 50.5

Weintek HMI (MT8071iE) is no longer reading inputs configured for digital units.
All of these inputs return the same reading as the IN2 configured for “Input Analog Units”

When we set up “Input Analog Units” for all inputs (range number = 34), HMI read then correctly again.
IN5 “Auto” and shorted.

Keeping these settings, everything works fine.