Updated: Here’s some general tips, turns out there was a bug whch Chelsea fixed as she replied below with the latest rev42 firmware.
[Earlier I wrote]: I suspect some of the inputs are configured as unused, you’ll get the 2.98V reading when there’s an open circuit / no sensor connected and the range is unused. Therange at Tab5 should be set to 10k Type2 or 3 as the case may be. Also in the inputs table, make sure the signal type at Tab10 is set as thermistor/dry contact.