Analog Output Limits

I notice that the outputs have a low limit and high limit setting. For what purpose do these settings have for analog outputs? Originally I was thinking that it limited the output in either direction for a 0-100% range but testing has proven that not to be the case.

Thank you

Reading old post, it seem it was suppose to be implemented to allow range or inverse, but still don’t seem to work.

Can anyone from TEMCO confirm about low/high limit?

It was aimed mainly at damper motors, a range of 0-100% would show 0-100% while the analog signal varied from 2-10V rather than the usual 0-10V. Its not used all that much since we also have a dedicated 2-10V (0-100%) range. I will have the team check that its still working and report back here in a couple of days.