Custom analog inputs

Here’s some screenshots showing how to configure transducers in general.
From the inputs table, click in the range column at Tab1 to bring up the range setting dialog with the various sensor types available and select ‘Custom Range’ 50 at Tab2 which brings up another dialog where you set up the signal table. At Tab4 you see the settings to plug in for a typical 4-20ma or 0-10V transducer at the minimum and maximum range of the sensor. You can also type in the engineering units at Tab5.

Finally, fill in the signal type in the inputs table at Tab6. The user interface is not great in the current version, you have to switch back and forth a couple of times to set up ma signal type.

To be done: Add a button to select the signal type near tab4 rather than have to back out and fill that in separately in the inputs table at Tab6.