The fun continued today. I believe I am having a bacnet conflict of some sort. Unsure if it’s a device name issue or instance id. The controller stayed online thru a variety of steps to understand where the issue was coming from. Ultimately, I was able to have the T3-8O stay online without issue when it was connected within my panel, with includes tridium running on a pc. No issue until i plugged in the network cable that connects to the BMS network with Alerton devices. Had planned for the T3 to be a bacnet device, but due to rebooting, I changed it to modbus. Even as modbus, I was rebooting until i changed the BIP to 47800 from 47808. I will need to do some wireshark play to see if i can find anything. Was definitely a discovery day.