Getting Started
First power up the transducer using a 15 to 24V supply, you can use either AC or DC. Next connec the RS485 network to the PC with an RS485 to USB converter. Connect just one device for now.
Pay attention to the polarity of the RS485 cabling, its OK to connect the A and B line in reverse, there will be no hardware damage but the device will not be able to communicate. It helps to have an RS485 converter with LEDS during troubleshooting.
Visit https://temcocontrols.com/ftp/software/09T3000Software.zip. Unzip and install the T3000 windows application. Start T3000 software, click the magnifying glass icon to scan for devices.
If all went well the device will show up in the left hand device list tree.
Click on the device in the tree to see the details and adjust them to suit the project. You can select the communications settings, the engineering units, calibrate the inputs and so on.
You can also click Tools->Register View to access the Modbus register list of the device. This shows the real time value of all the registers on the device. If bacnet protocol is selected you can use the Tools → Bacnet tool to see the bacnet objects and parameters.
TBD: Show bacnet mode.