maurice
November 26, 2022, 2:49am
2
The deivce comes completely blank state, you can follow along with any of the examples on the forum for single stage heat. I just completed one for single stage cooling here:
First head to the outputs table and configure the first stage cooling. At Tab1 we give the item a long 20 character name which is used in the graphics displays and floorplans. At Tab3 we give the output a short label which is used in the programming. At Tab2 you click in the ‘Range’ column to bring up the dialog with various ranges and select off-on.
[image]
Next head to the inputs table to configure the room temperature sensor. The sensor inside the Tstat10 case is at input #9 but any of the…