Hello friend, I have a T3-LB-W-1KPT controller installed in a hot water production system. I want to connect a pulse flow meter, such as the YF-S201C model. To connect a hall effect flow meter, what would be its connection diagram to the T3-LB-W-1KPT controller at the high speed pulse input. Or what other type of flow meter can I install?
Yes, connect to one of the high speed inputs, if the input is capable of high speed counting the option will show up in the range settings. There’s also a table here on the forum showing which device and inputs can handle the high speed counters.
The wiring diagram should be in our data sheets but I see that its not, we will add that after the local holiday. I would guess the black is GND and red is 5V to 12VDC power, then yellow is the signal.
You can generate the 5V supply by setting one of the analog outputs to 0-10V range and set it to manaully on and type in 5V for the value. Each analog output is capable of sourcing 100ma for powering small sensors like the hall sensor in the water meter.
Theres no known issues with pulse counting. To convert pulses to flow you will need to check your flow meter and make a simple formula like FLOW = PULSE / TIME. maybe I am missing something so you can let me know.