Valve modulating feedback signal of 2-10Vdc is connected to 1 out of 4 AI of Tstat7. At Input setup selection either 0-100% (2) or Voltage (14), the analog input displayed not the correct value. For example I used Voltage (14) mode if the input is 10Vdc, the displayed value is 11.97V. While when the input is 2Vdc, it displayed 8.00 Vdc.
There is a field just to the right of what you are showing here, its the signal type setting. Hopefully its there. The Tstat7 may not have all the options there.
Lijun will check into this with you. The two ranges are indeed what you need but it seems the Tstat7 is not behaving well. There is a calibration field that might help get you through this. More news soon.
I’m sorry, Tstat7 is an early product of ours and functions such as the range on the inputs are no longer sync’d up properly between the T3000 interface and the hardware. Normally we’d dig in and fix this but the people supporting this product have moved on. We’re planning a new version based on the ESP32 which will support all the functions and support of the latest T3 controllers and new Tstat10. The hardware is in layout now and we should have samples in a couple of weeks.