T3-OEM analog input issue

T3-oem only DC24V and RS485 connected. Controller AI reading voltage. That may cause issue?



image

Imput module is working, tried on another controller.

There is a weak pullup resistor for the dry contact/thermistor excitation voltage. Set the input sensor type to ‘voltage’ and this excitation voltage will not be active.