My goal is to add [non temco] modbus devices within the T3-XX network
Prior to that, I want to be sure that my modbus devices are working as expected.
I hooked my modbus unit with a temco usb-rs485 cable and tested through my modbus poll: ID, port, speed, etc. And the result is ok, I can harvest data in a regular manner.
Without touching anything (same computer, modbus cable and settings), I lauched the temco modbus poll program (within T3000 software) and tested my T3 (TCP): OK
However, when I try to change the TCP connection for the usb-rs485, I have100% connection errors (with the correct parameters).
Because of my previous tests, I know the connection is OK, but for unknown reasons, the T3000 Modbus poll failed on serial communication (I didnât try to reach my device through the main/sub rs485 because of this serial falure).
I tested the very same config with an old Temco unit (T3-8I13O) and I have the same problem through serial: The regular modbus poll program works but the Temco modbus program wonât.
Sorry to answer a question with another question, but could you give me a sketch of whatâs going on in the above setup. We think you are trying to poll to RS485 subnet devices from other manufacturers and using our T3-BB or similar as a general purpose IP to RS485 gateway.
If the assumption is correct then possibly the packets you are sending are not fully supported by our routing functions, our devices support routing for some modbus functions but not all of them. We mainly support the Modbus commands such as read & write registers used by Temco products, that is Modbus functions 03, 06, and 16.
Iâm not sure this will help your application but you can do some reading and writing to third party devices with a program running in the T3 controller. See the section titled âNetwork programmingâ in the link below for more info on how to do this:
Yes at first. The clear idea was to poll within T3 modbus adresses from third party modbus devices, taking advantage of the rs-485 main/sub network. Regarding your reply, I need to go further.
But. Because the result was not as expected, I hooked an old T3-8I13O and tried to add it automatically (scan) to see if the network scan worked.
The automatic scan was a failure (not detected, serial or main/sub). But was succesful if I added it manualy (add serial modbus device), including the integrated modbus poll from T3000 (latest version).
I tried then to follow the same pattern (add manual serial modbus device with its ID): failure
Maybe the T3-8I13O is too old to be recognized by the automatic scan and the third party modbus device is totally unable to be added into the T3 network, because of your answerâŚ
I wanted to be sure about my wirings and settings: I hooked a T8 to a T3 unit through my modbus sub and it was recognized right away with the automatic scan. So, it confirmed that the âculpritâ is the modbus connection between T3 units and third party modbus devices
Still having a tough time to envision what you are up to there Mike. If you are having trouble discovering devices on subnets you can connect directly over Ethernet and do a firmware update, do that from T3000 â help â check for updates. You should update both the T3000 front end and the device firmware while you are at it.
Also you can make use of the T3000 â tools â modbus tool to see the live Modbus registers of Temco devices at least (not the 3rd party devices though).
my post was about this, sadly. No probs to recognize temco devices (at least new ones like T8). I hoped to integrate 3rd party devices through T3 unit sub-rs485. If I canât see them or access them, I need to change my way to integrate them into my modbus network.
This T3-LB unit is for test only. Just a 10K temp sensor hooked and a time variable
Hooked a Peacefair Modbus Voltmeter (works in standalone mode with provided prgm and through my own modbus poll prgm and through serial-rs485 with node-red) into RS485 sub (2 stop bit, quite unusual).
Tried to access T3000 modbus poll (worked before -except the DST- the firmware update - was 51.0): received a âplease config the way of your connectionâ message instead.
Tried to modify data (same as a production T3-TB btw who can access built-in modbus poll) and obtained that message:
I tested this problem on two W7 computers (with latest T3000 software): same error
I downloaded T3000 software from your site (may 29 2020 .16) and ran it directly (no update) on a W10 computer (that had never seen T3000 software): NO error.
I updated (1.1.9) this T3000 on the same W10 computer and ran T3000 again (dec 24 2020 .14): same error
So it seems to me that this error is not related to the OS but seems to be related to the latest T3000 firmware.
So, if you want to use third-party devices (via modbus) and connect to Temco devices, you just have to configure one of the RS485 ports and just line up Unused ports (because third-party devices donât complete part of the command line that supports Temco).
Thanks Fance, I did it and I hope that will solve the problem.
But Iâm still unable to access modbus poll with the latest T3000 software (previous message).
2 choices for me: wait for a T3000 update or reinstall the orginal T3000 and use it without an update.
I tried.
If I use the latest T3000 software update, the time variable is ok (DST) but if I use the previous T3000 version, the modbus access is OK, but not the time variableâŚ
About the 3rd party access, with the âoldâ version of T3000, I can access modbus poll but the result is not OK. The network health is +/- ok (timeout), some RX
But when I harvest the modbus device, I canât poll data (write error) even I respect the parameters that works with other software.
I have just uploaded the latest T3000 software and fixed a possible exception message âPlease config the way of your connection!â when using the T3000 Modbus Poll.
I have also repeatedly verified just now that T3-BB TB-LB is able to access a third-party device normally by connecting it to a third-party device in the RS485-Sub Port and using the connection shown below. ()
The only thing to note is that RS485-MAIN and RS485-SUB cannot be set to âModbus Masterâ at the same time when connecting to third party devices.The implication is that one of them must be set to Unused.
If both ports are set to âModbus Masterâ, the T3 Controller will communicate in accordance with the configuration of RS485-Main port, and if you happen to connect the third party device to the SUB port, the communication will not be normal.
Please check again if the configuration information is wrong.
Updated T3000: OK, works as expected.
Connected my modbus device as requested and launched modbus poll: OK
tested the connection: KO, write error, whatever settings
Please Update T3000 again . Version : Jan 6 2021 . 14
Fixed a bug where the T3000 Modbus Poll established a TCP connection with the server and the connection was disconnected by the server, causing the communication to be unable to continue.
Bug phenomenon: Write Error after communication for some time.
Updated with the latest T3000 version (.14): OK
tried to poll modbus unit: failed
will install another 3rd party modbus device instead of my unit to see if the problem is consistent
thank you for your time
I really canât find the reason why you;re still experiencing problems.The following screen shot shows my connection as you describe your situation and here result here is completely fine.
I also use the command â04 Read Input Registers(3x)â , all works as expected.
We have both burned up a lot of time here, it would be best for us to do some remote assistance using Teamviewer or https://www.remoteutilities.com.
Please email and arrange a time to connect with you.
I really appreciate the help here.
But prior to this, Iâll hook another 3rd party modbus device that works differently (rs232-485, node-red, plc) and test the T3-LB behavior again with this.
If I have the same kind of problem with another device, Iâll let you remote control a computer with T3000 access.