I had effectively seen this sentence in the software manual but could not find how to display such pop up for the nano controller.
I read also somewhere that Nano would have ID 3? But this gave no result.
Another question is about the modbus bacnet register excel documentation found in the T3000 directory , this file mention only T3-BB controller but nothing for LB, TB or Nano controller.
Ok but where ?
Is it the parameter named
Modbus RTU ID:
Bacnet MSTP MAC
In the middle of panel information? Yes !!!
Now it works in the Modbus poll tools
And I can confirm that the Input are begining at address 7484 like BB controller
Input 3 is connected and give a value of 28723 in register 7489 corresponding to 28.72 for IN3 in the T3000
And VAR are from register 8092 and have the same format
So they must be simply read as long integer and rescale to real by dividing by 1000 … as I suspected yesterday