Tstat10e VAR3 MSV button selection not working
Hello, New to the forum and first post here.
I’m evaluating the Tstat10e and having problems with VAR3 set to SYS for OFF,HEAT,COOL.
It doesn’t matter if its set to AUTO or MANUAL on the Variable page.
I updated T3000 and Tstat10 to v67.4.
See this video. https://photos.app.goo.gl/i3HosmKR94FLc6Vk8
My simple test program is loaded below.
Any suggestions?
Thanks,
-srm
10 REM ***** 1801 WATERFURNACE TEST *****
20 REM VAR1 SET = SETPOINT
30 REM VAR2 FAN = 0 AUTO / 1 ON
40 REM VAR3 SYS = 0 OFF / 1 HEAT / 2 COOL
50 REM ***** REVERSING VALVE *****
60 IF SYS = 2 THEN START OOUT ELSE STOP OOUT
70 REM ***** HEATING *****
80 IF SYS = 1 AND ROOMTEMP < SET - 0.500 THEN START YOUT
90 IF SYS = 1 AND ROOMTEMP >= SET THEN STOP YOUT
100 REM ***** COOLING *****
110 IF SYS = 2 AND ROOMTEMP > SET + 0.500 THEN START YOUT
120 IF SYS = 2 AND ROOMTEMP <= SET THEN STOP YOUT
130 REM ***** SYSTEM OFF *****
140 IF SYS = 0 THEN STOP YOUT
150 REM ***** FAN ONLY *****
160 IF FAN = 1 THEN START GOUT ELSE STOP GOUT
170 REM ***** LCD ICONS *****
180 AY1[0] = 3
190 AY1[1] = 3
200 IF SYS = 0 THEN AY1[2] = 3
210 IF SYS = 1 THEN AY1[2] = 1
220 IF SYS = 2 THEN AY1[2] = 0
230 IF GOUT = 1 THEN AY1[3] = 1 ELSE AY1[3] = 0
Lijun will check into this with you in 2 days, there’s a short holiday here just now.
The latest rev67.8 firmware has fixed the issue where the MSV value cannot be modified via the keypad. I have uploaded it to FTP.
Chelsea,
Thanks for fixing the buttons, but it would be nice if they worked consistently?
Also, the occupancy sensor isn’t work, unless there is something I’m missing on the setup?
See video showing both… https://photos.app.goo.gl/ubhh4isUt7Cf1Z2o6
Thanks,
-srm
No additional settings are required for the occupancy sensor. Please note that the T3000 interface refreshes only every 15 seconds. When you perform the test, you need to read the input promptly to see the status change of the occupancy sensor.