Since then the “old” trend-log function does not work. It loads the graphic screen with channel key and time axis, but no data - either analog or digital. The SD card memory-used does not increase.
Has the “old” trend-logging system been discontinued?
I have resisted setting up the “new” trendlogging system. Has it moved beyond Beta yet?
The main reason I do not use the “new” system is the use limitations (ie that T3000 must run continuously to maintain recent logging). I want to be able to see “last-night’s” data, which the old system provides “approximately” based on SD card data
The old trend log has not been discontinued, and the new system is still in Beta.
One possible cause is opening the new trend log while using the old system. Even without collecting data in the new system, this can disrupt the SD card log data and prevent the old trend log from working.
If this has happened, the affected log needs to be deleted and logging restarted. This will remove its existing history. To avoid the issue, please do not open the new trend log while using the old system.
Thank you. Please confirm what is required to delete the old log? I currently have 3 different multi-channel monitors that I use selectively. For one of these - I deleted the 9 channels (1 x 1) and selected OFF, deleted channel data, then reentered the 9 channels - but I still do not get any traces. I get the data loading “indicator wheel” which gets to 1% then disappears.
I rebooted the T3_BB and the traces have restarted.
However, if I close the trend monitor window the analog datapoints do not display but resume when I reopen that monitor. The digital datapoints display continuously The SD card status is normal.
Hi,
I have been and still am using the OLD version with SD card.
The guidelines for the NEW version say that trend data is not stored in memory unless T3000 is running - ie when T3000 is not running, data capture stops.
I generally run T3000 by remote access and close T3000 between remote access sessions. It is a real limitation that I have to keep T3000 running ALL the time - I dont have control of PC except during remote sessions. The old Trend display is able to (background) store data in SD card even when T3000 is not running - and retrieve SD card data in the next T3000 session. This is the main reason I have not changed to the new version.
Have I misunderstood the requirements/limitations?