Input32, does not report data via modbus tcp, but it does show correctly in T9000 as well as BACnet IP. Is this already a known bug in the works to being fixed?
Edit: You can also easily check this by using the Register Viewer in T9000.
I know that with bacnet the range has to be set to something other than unused. Lijun will test and see if he can duplicate your issue.
Thanks,
For further info for Linjun, the problem isn’t BACnet, it works fine in BACnet, it is in Modbus TCP (maybe RTU as well, did not test). All the other inputs are setup exactly the same way and they work as expected, it is just input 32 that has the issue. In T9000 using the Register Viewer it does not work either.
Thanks for pointing this out.
We confirmed that this was a software bug in the Modbus handling for Input 32. The issue has now been fixed. Please update the firmware to the latest version and check again.
Working! Thank you very much!