Is it possible to set-up a limit for PID higher value and lower value?
Ex: We need a VFD to ramp only between 35 Hz and 50 Hz accordingly maximum & minimum values to be set/freeze at 50 & 35 respectively.
There are two topics that can help you:
(Setting up upper & lower limits in PIDs)
Maurice shows an example to limit the output value.
(Converting 4-20ma signal to actual value using a program)
Maurice shows an example of how to use the straight line formula to convert signals and, of course, it can be used to convert the 0% / 100% PID output to 35Hz / 50Hz (58.33% / 83.33% )
I like to clip values using this MIN nested inside a MAX statement, its easy to see what’s going on.
VFD = MAX( 35 , MIN( 50 , PID1 ) )
Thanks for the help Adalberto. Glad to see folks are finding the forum useful.