Hi!
I want to use a Tstat10 within a Modbus RTU context.
I connected a PT1000 sensor on UI2 (for instance) and configured the IN2 as a 10K Type2, reading °C, using T3000 software.
The value given by the inputs view in T3000 is 87.80 °C which seems pretty high as a room temperature ;-).
I tried wiht a 10K Type3 configuration, but it is even worse.
The PT 1K -200 to 300 option cannot be activated.
What is wrong with my approach?
Register view gives the same value through registers 7486-7487 which corresponds to 1 and 22264 with Modbus Poll being the same 87800 value.
Thank you in advance.
Sorry for the slow reply. The reason the 1k Pt option cannot be selected is that the Tstat10 doesnt support the 1k Pt type sensors. There’s a small amount of circuitry involved and unfortunately the Tstat10 doesnt have it on board. There’s a few of the T3 series controllers which support 1k Pt but its always as an option during checkout whether to add 1k Pt support or not.