Hi Guys, just to preface this, I did read the following post T3-TB as a BACnet/MSTP router question - Troubleshooting - Temco Controls Forum, and I am coming to the same issue.
I have a TB-8i with a Neptronic HROB20 humidity controller on MSTP MAC 20, with an instance ID of 120, and a Contemporary Controls BAST-221C-B2 Thermostat on MSTP MAC 15 and a instance ID of 15. Port is at 38400 on all devices, comms are good:
SO! The Neptronic is reliable and DOES show up, and when I poll the variables, all is good :
The Thermostat on the other hand will NOT show up under the device tree in T3000, and while I can send and poll using YABE launched from the T3000 application, But the YABE on my laptop on the same subnet (Windows 11, YABE version 2.10) can SEE the devices, but the WhoIS fails every time. Also, the variables do not update reliably.
So, two questions: 1.) Did I miss a step with the thermostats? 2.) How the hell do I write to the variables? I can read AI’s, AO’s, BI’s, BV’s, and MSV’s, but cannot write to them from the T3000 interface, whether it is in auto or Manual mode. I am assuming that I am doing something wrong. I have just ordered two TB tiny’s to use as BACnet routers as opposed to the Contemporary Controls BASRT-B’s that I normally use, as I have a location that we want to add 100+ TB tiny’s as routers. For an HMI, we use both a Weintek HMI as well as BASView 3.
Let me know if you need any more info!
Thanks!