I try to set the PID , but failed.
For example:
- Cool
IF TEMP > TEMPS + BIAS THEN ABOVE OUTPUT //PID+ - Hot
IF TEMP < TEMPS - BIAS THEN BELOW OUTPUT //PID- - IF ABS(TEMP-TEMPS)<BAIS THEN OUTPUT=OUTPUT //PID=PID
How to set this Function ?
I try to set the PID , but failed.
For example:
Try this:
10 COOLVLV = PID1 <The cooling valve will follow a PID set up in cooling mode.
20 HEATVLV = PID2 <The heating valve will follow a PID set up in heating mode.
30 REM ***** CLOSE THE VALVES WHEN THE FAN IS NOT RUNNING *****
40 IF NOT FANSTAT THEN COOLVLV = 0
50 IF NOT FANSTAT THEN HEATVLV = 0