T3-6CTA CT inputs range

Unfortunately not in this time. There was no change log in the window.

The chang log has shown now

Dear Spring,

Please check the firmware again. After update UI 1 & 2 works as 10 & 11 in T3000 and ModBus registers. The same with 3&4 (moved to 4&5). Other inputs I didn’t check.

OK , I have checked the firmware which is good , I take two pictures about the label of T3-6CT and
INs shown in T3000 for your reference.



It seems that I have another type.

Its just a different label on yours. Underneath the electronics are the same.

Unfortunately not only the LEDs were changed in mentioned firmware. Inputs in T3000 and ModBus were changed also. After downgrade to T3_6cta_Type1&2_28 everything get normal back.

Use the T3000 application → Tools → Modbus register Viewer to check the modbus registers.

image001.jpg

I’m sure they are different in Type1&2 firmware and Type4. But it doesn’t mater, I downgraded and wait for CTs from AliExpress.